cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/10/2008 6:21 PM

Dear All,

good day.

I have one 1000 KVA diesel engine. Aproximately 350KVA load is for one cold room refrigeration units, 450 KVA for a processing plant.

I wanted to calculate the diesel consumed by the coldroom units seperately. I am planning to put a KWH meter on the load to calculate the units consumed by the cold room.

Needs suggestions and formula's for calculating the ltrs of diesel for the consumed KWH. Also any other suggestions to calculate the diesel quantity per month.

How to arrive the diesel in ltrs related tothe no of units consumed.??

Thanks,

Kannan

__________________
kannank
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/10/2008 6:54 PM

Hello kannanksundaram

Best for you would be a fuel flow totalling type meter on the fuel line to each engine.

See picture at left.

Refer: http://www.dealtime.com/-diesel+fuel+meter

Such a meter will give you correct fuel consumption, and the readings may be taken as often as you wish.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2007
Location: I am located in Mumbai,India.
Posts: 125
Good Answers: 2
#2

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/11/2008 10:57 PM

The average generation of power ranges from 3 to 3.5 kwh per litre of diesel depending on the load on the generator and how well the generator is maintained. By measuring kwh consumed by cold room, you can calculate the diesel consumed for cold room purpose.

__________________
Rajesh
Register to Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#3

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 3:46 AM

Most accurate method would be to meter oil consumption and both electric loads and the apportion the oil in the ratio of the electric consumptions.

Register to Reply
Anonymous Poster
#4

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 3:58 AM

Normally units generation 3 to 3.5 per ltr of HSD at 1000 KVA load,

as u are operating at 800 kva(350+450), it will be aproximate 3 units/lts.

if HSD cost is Rs 30/ltr(for example) then per unit cost become Rs 10.0

calculate total unis on basis of cold room actual units, suppose total units of cold room will be 3500 per day then as per load condition units of other section will be 4500, so total units become 8000 units @ 3unit/ltr ie 8000/3 ltr diesel u required for one day....

Register to Reply
Associate

Join Date: Aug 2007
Location: New Delhi, India
Posts: 33
#5

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 4:37 AM

Dear Kannan

For calculating the fuel consumed by cold storage you require to know the total fuel consumed by the DG set. You need to know the total units generated by the DG set and units consumed by the cold storage.

Let Total diesel consumed in 2 hours is 450 ltrs.

Total units generated in two hours is 1500 KWh.

Total units consumed by cold storage be 600 KWh.

This states that units consumed by process plant is 900 KWh.

DG set efficiency per liter comes out to be 3.33 KWh/ltr.

Hence diesel consumed by Cold storage is 600/3.33 and process plant is 900/3.33. Hope it clears your doubt and you can predict the deisel required.

__________________
Ashish Gupta
Register to Reply Off Topic (Score 5)
Anonymous Poster
#6

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 5:50 AM

The efficiency of a DG set varies with the % of load.

Usually , for best results the DG should be loaded to appx 90 % of its rated load.

In order to get the best results from the DG sets it needs to be maintained well & loaded wisely .

Considering following assumptions :

1] LCV of fuel - 10000 lcal/kg & efficiency of DG set 35 %

Units that can be generated - (10000*0.35)/860---4.06 Kwh

Accordingly, putting the values for your DG set efficiency & LCV of the HSD you can find out the power that can be generated, theoritically.

BKK

Register to Reply
Anonymous Poster
#14
In reply to #6

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

11/25/2008 2:40 AM

How have to calculated this what is 860 , prevailing industry norms are 3 to 3.5 Kwh per ltrs

Register to Reply Off Topic (Score 5)
2
Commentator

Join Date: Jun 2008
Location: Brick, NJ
Posts: 71
Good Answers: 8
#7

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 6:15 AM

As I read all these comments and then go back and read your original post, you don't mention a couple of things. Do you have a fuel meter on the engine now? If not, you'll need two of them for a diesel. One one the supply and one on the return line. Subtract them out to get the fuel consumed. An easy way to get a 24 hour average without a meter is to measure the fuel in the storage tank and calculate liters used in 24 hours. Also you say you will be putting a kwh meter on the cold room. You also need a kwh meter on the diesel generator or on the main swtchboard before it is distributed. If you cannot, then you cannot get the percentage of the fuel used by the cold room. You are using round numbers for the estimated loads and the other numbers people are suggesting are fine textbook numbers for planning purposes. However, the loads do not run that way during normal operation. Your coldbox will be affected by outside temperature no matter how well insulated. Plant loads will vary depending on the state of the process.

What you are most likely to be interested in is an average rather than instantaneous fuel flow. You need to calculate total number of liters used divided by total kwh produced to get l/kwh. The multiply by kwh consumed by the cold box. You would want to do this daily for at least a week to be sure that you get a good average.

Without an accurate number of liters used and an accurate number of kwh produced, you are guessing and the calculation of liters that are going to the cold box are meaningless.

__________________
Do this. Don't do that. Can't you redesign?
Register to Reply Good Answer (Score 2)
Associate

Join Date: Aug 2007
Location: New Delhi, India
Posts: 33
#8
In reply to #7

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 6:24 AM

yup...

This needs to be done if not yet in place.

__________________
Ashish Gupta
Register to Reply
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#9
In reply to #7

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 2:13 PM

I agree in a general sense. However the flows can also be calculated from specific fuel consumption figures for the diesel and efficiency for the generator. (Often this is already done by the generator vendor.) I'm guessing that this may be sufficient for the poster's purposes, and would not require any additional equipment and installation thereof.

My guess is that the poster just needs to apportion fuel usage for accounting purposes, and that he already knows the total fuel usage, on average, for the generator. In that case, he could split the fuel use according to the energy split.

Otherwise he would need different figures for different loading conditions : one unit, the other unit, both units, etc. My guess is that's more detail than he needs, but who knows?

__________________
There is more to life than just eating mice.
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#10
In reply to #7

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/12/2008 5:21 PM

Hello andrew_ward

from me

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
Participant

Join Date: Aug 2008
Posts: 2
#11

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/13/2008 3:45 AM

hi..

first u should calculate how much diesel will utilise to produce one KWH. Then you put a KWH meter for your cold room and processing sections. We can produce 3.5 KWH from one litre of diesel. . i think it will be usefull to u.

Register to Reply
Commentator

Join Date: Mar 2006
Location: Sydney, Australia
Posts: 96
Good Answers: 5
#12

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

09/13/2008 9:39 AM

Socomec Countis CI counters can accept 7 pulse inputs. 2 of these would connect to the supply and return fuel lines for your generator via paddle wheel pulse flow meters.

Then install 2 x Socomec Diris A40 meters - 1 for the cold room and the other for the processing plant.

The meters connect back to a PC running XP via RS485 (fairly typical Modbus protocol)

Smart EE software then monitors the 3 meters and will give you minute by minute [or second by second] recording monitoring and exports the data to Excel where you may further refine it.

Here is an example of 2 power meters logged per minute on one of our installations.

__________________
Mark Taylor, Senior Technical Advisor, CV Bli Tek, Bali, Indonesia.
Register to Reply
Anonymous Poster
#13

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

11/04/2008 4:43 AM

No worries Mr.Kannan. In the present technological context, the average units generated per liter of diesel is around 3.5 on a moderately maintained generating sets. Catterpillar claims around 4 units per liter under any load conditions. Yes you are right. Install energy meters for two loads separately. There should be one KWh meter installed for DG set as well. Best method of finding out fuel consumption for your loads is to run each one separately, if your process permits, on a weekend for 2 hours. To calculate the fuel consumption, there are two methods: i) Install a flow meter in the suction line of the fuel pump near the tank (very reliable & accurate) ii) If the fuel is flowing from a day tank, note down the INITIAL LEVEL (say L1) & INITIAL KWh reading (say W1). Start the DG set & give one load at a time & run for, say, 2 hours. Now measure the FINAL LEVEL (say L2) & FINAL KWh reading (say W2) Energy generation, units per liter = (W2-W1) / (L2-L1) Otherway, liter per units = (L2-L1) / (W2-W1) Let me know if this helps you. Of course there are good electronic gadgets available to measure the same parameters, but does not justify the investment for one DG alone.

Register to Reply
Anonymous Poster
#15
In reply to #13

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

02/13/2009 12:07 AM

every one i want to tell u that i need any equipment how calculate the diesel consumption of generator by the voltage? thanks for corp.....................

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: cALCULATE DIESEL IN LTRS BY FIXING AN KWH METER ON LOAD.

12/15/2023 4:01 AM

Try this:

  • Put a totalising flowmeter on the fuel line to one of the units.
  • Get a dipstick, a tape measure and a clock.
  • The rate of consumption of <...diesel...> to one unit is measured by the flowmeter.
  • The rate of consumption of both units is measured by the dipstick, the tape measure and some arithmetic based on the shape and levels of the storage tank.
  • Subtract one from the other to get the consumption of the second unit.

Simplesξ.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

andrew_ward (1); Anonymous Poster (5); ashuashi (2); Blink (1); Gasman (1); gsk_ckd@rediff.com (1); PWSlack (1); rsalaskar (1); Sparkstation (2); Tamu (1)

Previous in Forum: Z-Folding Equipment   Next in Forum: structural shim/filler analysis

Advertisement